| ??? 04/27/10 12:01 Read: times |
#175436 - well Responding to: ???'s previous message |
You have some readymade RTU SLAVE device and You are trying to build Your master device. If so - try first to connect RTU SLAVE to PC master , not to Your master. Her You can connect other PC to monitor serial conversation , or run on same PC underlaying software monitor/recorder for serial COM events.
If You are trying to buld SLAVE - same thing - USE MODBUS MASTER PC , probably with (nderlaying monitor/logger on serial COM . Or instead underlayng monitor - connect other PC to listen what MASTER and SLAVE talking aobout. regards |
| Topic | Author | Date |
| modbus | 01/01/70 00:00 | |
| there can be | 01/01/70 00:00 | |
| simulator | 01/01/70 00:00 | |
| Modbus simulators | 01/01/70 00:00 | |
| well | 01/01/70 00:00 | |
| choice or requirement? | 01/01/70 00:00 | |
| Asm code search.. | 01/01/70 00:00 | |
thanks | 01/01/70 00:00 |



