K. said:
However, the external RS485 device has no provision to connect Ground line. The external RS485 device belongs to a "large" "reputed" manufacturer and they feel that lack of ground connection can not be the reason for failures as it is working in installations in some other parts of the world!

Of course, but remember that you told

The earthing on the 230V supply point is not good and some times a voltage of 90+V is found between Neutral and Earth.


With such huge common mode interference you cannot omit the signal ground connection in the RS485 interface! The next failure you observe can be the RS485 transmitter, if the common mode interference is really that huge...

Yes, I know, not the RS485 transmitter has failed but the RS232. But let me tell you, that I have learned over the years, that interference taking place at the one point can have influence on a different point, even if you might not understand how, at the first moment...

Kai

List of 9 messages in thread
TopicAuthorDate
MAX232 failure            01/01/70 00:00      
   MAX232 failure            01/01/70 00:00      
   Does that mean, ...            01/01/70 00:00      
      Yes, ground is not connected            01/01/70 00:00      
         exactly what is connected to the MAX232...            01/01/70 00:00      
         But it truly should...            01/01/70 00:00      
            Thanks for your suggestion            01/01/70 00:00      
               485/232 with 'unreliable' ground            01/01/70 00:00      
   It is a handheld terminal            01/01/70 00:00      

Back to Subject List