Damjan Lapuh said:
I try to avoid addressing because customer can install/replace sensor by himself and work does not require any additional settings.

Of itself, this doesn't need any settings at all!
Each sensor has a unique ID, and the system can determine the number & IDs of sensors attached automatically - See Dallas documentation for details. (of course that would need extra code space - that you don't currently have!)

The problem comes if you need to relate a specific device ID to a specific temperature measurement; eg, "which sensor monitors motor No 1?" or "which sensor is in the Living Room?"
See: http://www.8052.com/forum/read.phtml?id=67682