#118240 - Open "E1" and have a look at
Responding to: ???'s previous message
Ganeshan said:
I notice that it's powersupply has an unusually large transformer. Looks like a toroidal transformer.

Yes, they are large indeed! Once I measured some nF with a 500VA toroidal mains transformer. In this case a 100nF cap between PE and signal ground (of RS485) at "E1" should suppress the mild shock.

Nevertheless, this doesn't explain the malfunction of your RS485 loop. Look whether the "E1" has a proper termination resistance at its input and use a LT1785 as driver.

Take also care about what Erik stated: If two or more such devices "E1" are connected, then only one termination resistor at the recieveing side is allowed: One at the driver and one at the farest distanced reciever. I assumed, that only one such device "E1" is connected.

Kai

List of 14 messages in thread
TopicAuthorDate
Bad MAX 485 IC ?            01/01/70 00:00      
   Voltage between Earth and Neutral..            01/01/70 00:00      
      also            01/01/70 00:00      
         This may be one reason            01/01/70 00:00      
   What's a DB9?            01/01/70 00:00      
      Correction . DE9 - not DB9            01/01/70 00:00      
         Earthed Shell to the shield of cable            01/01/70 00:00      
   Mild shocks...            01/01/70 00:00      
      E1 is a pump controller            01/01/70 00:00      
         Open "E1" and have a look at            01/01/70 00:00      
      you missed one            01/01/70 00:00      
         Only one reciever            01/01/70 00:00      
            Yes. Only one receiver            01/01/70 00:00      
               all uC developers should be Boy Scouts            01/01/70 00:00      

Back to Subject List