The hazards of using half-duplex RS-485 is that if any node fails in transmit mode it will jam the entire network. From the description I would guess a particular controller fails with the transmit enable line to the MAX1483 turned on. It's not the MAX1483, it's the 89C51 that's the problem.
For 24/7 reliability you will need some kind of watchdog/failsafe circuit that ensures the RS-485 transceiver disconnects if the controller fails. You might look at using some kind of one-shot to enable the transmit, which then times out until the next enable pulse from the controller. |