erik malund wrote:
-------------------------------


By the way, the above remind me, I have seen ever so often designs where the ADC was used full scale i. e. max normal input = max value. That is a BIG mistake. In such a design there is no way to detect an error causing the analog input going wild because of an open or short.



That reminds me of a not-so-funny story. In a first version of a product using a 16-bit ADC to read temperature via RTDs wired through a 1K pull-up resistor, the system would periodically select a channel with a hard-wired 1K pull-down resistor. If the channel read 2.5 Volts (8000H), the system determined that all was good.

Well, it turned out that the ADC could lose its calibration data and then when it would take a reading, it would take the reference (which was 8000H) multiply it by the gain (which defaulted to 1) and add the offset (which was then 0) and come up with 8000H.

The moral of the story is to be careful when you choose you error checking. It helps to try to predict (or simulate) the method of failure when you design your error checking.

-- Tom Bachmann

List of 39 messages in thread
TopicAuthorDate
Error logging for purpose of Maintenance            01/01/70 00:00      
   RE: Error logging for purpose of Maintenance            01/01/70 00:00      
      RE: Error logging for purpose of Maintenance            01/01/70 00:00      
         RE: Error logging for purpose of Maintenance            01/01/70 00:00      
            RE: Error logging for purpose of Maintenance            01/01/70 00:00      
               RE: Error logging for purpose of Maintenance            01/01/70 00:00      
                  RE: Error logging for purpose of Maintenance            01/01/70 00:00      
                     RE: crash- spelling error            01/01/70 00:00      
                  RE: CRASH routine            01/01/70 00:00      
                     RE: CRASH routine            01/01/70 00:00      
                  RE: ADC input Error logging            01/01/70 00:00      
   RE: Error logging for purpose of Maintenance            01/01/70 00:00      
      RE: Error logging for purpose of Maintenance            01/01/70 00:00      
   Ten percent            01/01/70 00:00      
      RE: Ten percent            01/01/70 00:00      
   RE: Error logging for purpose of Maintenance            01/01/70 00:00      
      RE: Error logging for purpose of Maintenance            01/01/70 00:00      
      RE: Error logging for purpose of Maintenance            01/01/70 00:00      
   RE: Error logging for purpose of Maintenance            01/01/70 00:00      
      RE: Error logging for purpose of Maintenance            01/01/70 00:00      
         RE: Error logging for purpose of Maintenance            01/01/70 00:00      
            RE: Error logging for purpose of Maintenance            01/01/70 00:00      
               RE: Error logging for purpose of Maintenance            01/01/70 00:00      
                  RE: Error logging for purpose of Maintenance            01/01/70 00:00      
                  Accessing logs            01/01/70 00:00      
                     RE: Accessing logs            01/01/70 00:00      
                        RE: Disappearing RS232            01/01/70 00:00      
                           RE: Disappearing RS232            01/01/70 00:00      
                  RE: Error logging for purpose of Maintenance            01/01/70 00:00      
   RE: Error logging for purpose of Maintenance            01/01/70 00:00      
      RE: Error logging for purpose of Maintenance            01/01/70 00:00      
   RE: Error logging for purpose of Maintenance            01/01/70 00:00      
      RE: Error logging for purpose of Maintenance            01/01/70 00:00      
   RE: Error logging for purpose of Maintenance            01/01/70 00:00      
      RE: Error logging for purpose of Maintenance            01/01/70 00:00      
      RE: Error logging for purpose of Maintenance            01/01/70 00:00      
         RE: Error logging for purpose of Maintenance            01/01/70 00:00      
            RE: Error logging for purpose of Maintenance            01/01/70 00:00      
               RE: Error logging for purpose of Maintenance            01/01/70 00:00      

Back to Subject List