#127946 - Sounds like an earthing problem Responding to: ???'s previous message |
Kiran,
If you only connect one variable speed drive, play around with the different possibilities of the RS485 shield to earth or to ground. Is the cable from the VSD to the motor shielded? And properly earthed? Is there any change when you remove the 100R resistor (in many cases this is not necessary of the data rate is low and/or the cable length is short). |