#171355 - Don't use hyperterminal
Responding to: ???'s previous message
For modbus tests, there are plenty of software for checking frames with PC. For example, Modbus Poll.
Why PLC does not answer:
- Baud rate
- Parity
- Hardware
- RTU or ASCII?
- Incorrect CRC16
- Function not implemented
- ....

Daniel


List of 27 messages in thread
TopicAuthorDate
Modbus            01/01/70 00:00      
   What testing have you done?            01/01/70 00:00      
   Don't use hyperterminal            01/01/70 00:00      
   modbus            01/01/70 00:00      
      modbus            01/01/70 00:00      
         Still lots of debugging left            01/01/70 00:00      
            Modbus            01/01/70 00:00      
               Not very helpful            01/01/70 00:00      
                  Modbus            01/01/70 00:00      
                     Still need to break the problem down into smaller steps            01/01/70 00:00      
                        Modbus            01/01/70 00:00      
                           modbus            01/01/70 00:00      
                              modbus            01/01/70 00:00      
                                 Parity            01/01/70 00:00      
                                 Oscilloscope results?            01/01/70 00:00      
                                 open source            01/01/70 00:00      
                        Also RTU Framing            01/01/70 00:00      
                           Framing, addressing etc has been discussed            01/01/70 00:00      
                              modbus            01/01/70 00:00      
                                 Bad CRC order!!            01/01/70 00:00      
                                    modbus            01/01/70 00:00      
                                       modbus            01/01/70 00:00      
                                       Don't know why,            01/01/70 00:00      
                                       Comparison with something known working            01/01/70 00:00      
                     what device address            01/01/70 00:00      
                        modbus            01/01/70 00:00      
   I would do this...            01/01/70 00:00      

Back to Subject List