12/02/09 06:49
Read: times


 
#171376 - Still lots of debugging left
Responding to: ???'s previous message
So, if the Hyperterminal doesn't get any answer, then you shouldn't expect your microcontroller to get any answer either, should you?

Does the modbus test programs receive any answers? If they do, then your first job is to figure out the difference between requests from them contra the manual requests you send out using the Hyperterminal. If they don't, then you have to figure out if you have correctly configured them, and if your cabling is correct and if the modbus protocol has been enabled in the external device etc.

My question is still: What have you tried to do to figure out where the problem is?

How do you know that 9600 baud is the correct speed?
How do you know that there shouldn't be any parity?
How do you know that your null-modem cabling is correct?
How do you know that your null-modem cabling is correctly connected?
How do you know that the device is using RTU?
How do you know that the device have Modbus enabled?
How do you know that the request is reaching the device?
How do you know that the device isn't answering, but the answer not reaching the PC?
How do you know that your timing is ok?

List of 27 messages in thread
TopicAuthorDate
Modbus            01/01/70 00:00      
   What testing have you done?            01/01/70 00:00      
   Don't use hyperterminal            01/01/70 00:00      
   modbus            01/01/70 00:00      
      modbus            01/01/70 00:00      
         Still lots of debugging left            01/01/70 00:00      
            Modbus            01/01/70 00:00      
               Not very helpful            01/01/70 00:00      
                  Modbus            01/01/70 00:00      
                     Still need to break the problem down into smaller steps            01/01/70 00:00      
                        Modbus            01/01/70 00:00      
                           modbus            01/01/70 00:00      
                              modbus            01/01/70 00:00      
                                 Parity            01/01/70 00:00      
                                 Oscilloscope results?            01/01/70 00:00      
                                 open source            01/01/70 00:00      
                        Also RTU Framing            01/01/70 00:00      
                           Framing, addressing etc has been discussed            01/01/70 00:00      
                              modbus            01/01/70 00:00      
                                 Bad CRC order!!            01/01/70 00:00      
                                    modbus            01/01/70 00:00      
                                       modbus            01/01/70 00:00      
                                       Don't know why,            01/01/70 00:00      
                                       Comparison with something known working            01/01/70 00:00      
                     what device address            01/01/70 00:00      
                        modbus            01/01/70 00:00      
   I would do this...            01/01/70 00:00      