#171373 - modbus Responding to: ???'s previous message |
@Per Westermark:
Hyper Terminal is not getting any answer from PLC. Baudrate is 9600, 8-N-1, there is null modem configuration. @Daniel Contarino: I have tested the PLC at modscan and the reply is fine. Why PLC does not answer: - Baud rate---------------------9600 - Parity------------------------No parity - Hardware----------------------Null Configuration - RTU or ASCII------------------RTU - Incorrect CRC16---------------In that case the PLC should response with an error message, but no reply - Function not implemented------All necessary functions are implemented Thanks. |
| Topic | Author | Date |
| Modbus | 01/01/70 00:00 | |
| What testing have you done? | 01/01/70 00:00 | |
| Don't use hyperterminal | 01/01/70 00:00 | |
| modbus | 01/01/70 00:00 | |
| modbus | 01/01/70 00:00 | |
| Still lots of debugging left | 01/01/70 00:00 | |
| Modbus | 01/01/70 00:00 | |
| Not very helpful | 01/01/70 00:00 | |
| Modbus | 01/01/70 00:00 | |
| Still need to break the problem down into smaller steps | 01/01/70 00:00 | |
| Modbus | 01/01/70 00:00 | |
| modbus | 01/01/70 00:00 | |
| modbus | 01/01/70 00:00 | |
| Parity | 01/01/70 00:00 | |
| Oscilloscope results? | 01/01/70 00:00 | |
| open source | 01/01/70 00:00 | |
| Also RTU Framing | 01/01/70 00:00 | |
| Framing, addressing etc has been discussed | 01/01/70 00:00 | |
| modbus | 01/01/70 00:00 | |
| Bad CRC order!! | 01/01/70 00:00 | |
| modbus | 01/01/70 00:00 | |
| modbus | 01/01/70 00:00 | |
| Don't know why, | 01/01/70 00:00 | |
| Comparison with something known working | 01/01/70 00:00 | |
| what device address | 01/01/70 00:00 | |
| modbus | 01/01/70 00:00 | |
I would do this... | 01/01/70 00:00 |