#171380 - Still need to break the problem down into smaller steps
Responding to: ???'s previous message
No need for bold text. Your Modbus test programs probably already knows how to talk Modbus.

1) Connect PLC to PLC.

2) Look at the serial data between them. What baudrate? Parity?

3) Connect PC to PLC.

4) Does the serial data reaching the PLC look the same?

5) Create a sniffer cable where the RX signal from PLC1 to PLC2 is sent to one serial port on PC, and the TX signal to another serial port on the PC.

6) What data does the PC pick up from PLC1? What data does it pick up from PLC2? What is the difference compared to the info your PC tries to send?

Your task is to figure out the difference between the combinations that works, and the combinations that doesn't work. Either reading all documentation and figuring out what may be wrong. Or by using a bit of test equipment and measuring what is happening, and comparing to what you expect should happen.

List of 27 messages in thread
TopicAuthorDate
Modbus            01/01/70 00:00      
   What testing have you done?            01/01/70 00:00      
   Don't use hyperterminal            01/01/70 00:00      
   modbus            01/01/70 00:00      
      modbus            01/01/70 00:00      
         Still lots of debugging left            01/01/70 00:00      
            Modbus            01/01/70 00:00      
               Not very helpful            01/01/70 00:00      
                  Modbus            01/01/70 00:00      
                     Still need to break the problem down into smaller steps            01/01/70 00:00      
                        Modbus            01/01/70 00:00      
                           modbus            01/01/70 00:00      
                              modbus            01/01/70 00:00      
                                 Parity            01/01/70 00:00      
                                 Oscilloscope results?            01/01/70 00:00      
                                 open source            01/01/70 00:00      
                        Also RTU Framing            01/01/70 00:00      
                           Framing, addressing etc has been discussed            01/01/70 00:00      
                              modbus            01/01/70 00:00      
                                 Bad CRC order!!            01/01/70 00:00      
                                    modbus            01/01/70 00:00      
                                       modbus            01/01/70 00:00      
                                       Don't know why,            01/01/70 00:00      
                                       Comparison with something known working            01/01/70 00:00      
                     what device address            01/01/70 00:00      
                        modbus            01/01/70 00:00      
   I would do this...            01/01/70 00:00      